For those of you attending MACNA this coming weekend, keep an eye out for me demonstrating a prototype of my Alkalinity Monitor device. It is capable of interfacing with any controller that can accept a pH probe's input. It has both an accuracy and also a precision of +/- 0.05 dKH. I'm thinking this could be a game changer.

Here is an Apex graph of two day's worth of monitoring of my tank, showing a small daily alk swing in response to the photoperiod:

Diurnal%20Alkalinity%20Swing%20-%20Two%20Full%20Days_zpsbunbn6zk.png
 

Sabellafella

7500 Club Member
View Badges
Joined
Jul 8, 2015
Messages
7,547
Reaction score
11,873
Rating - 100%
5   0   0
When should we expect the thread on this to popup ;)
For those of you attending MACNA this coming weekend, keep an eye out for me demonstrating a prototype of my Alkalinity Monitor device. It is capable of interfacing with any controller that can accept a pH probe's input. It has both an accuracy and also a precision of +/- 0.05 dKH. I'm thinking this could be a game changer.

Here is an Apex graph of two day's worth of monitoring of my tank, showing a small daily alk swing in response to the photoperiod:

Diurnal%20Alkalinity%20Swing%20-%20Two%20Full%20Days_zpsbunbn6zk.png
 
OP
OP
JimWelsh

JimWelsh

Valuable Member
View Badges
Joined
Nov 5, 2011
Messages
1,547
Reaction score
1,680
Location
Angwin, CA
Rating - 0%
0   0   0
Here is a graph where I programmed my Apex to control alk dosing in response to the monitor's output so as to keep it right at a target value, 8.0 dKH in this instance.

Here is the Apex program for the Outlet that controls the alkalinity dosing pump:

Fallback OFF
OSC 000:00/000:44/006:10 Then ON
If Alk > 08.00 Then OFF
If Alk < 07.10 Then OFF

The reason for the "If Alk < 07.10 Then OFF" line is that if my device were to ever lose power for whatever reason, the output would drop to 7.0 (same voltage as a pH probe at pH 7.0 = 0.0 volts). In that case, I don't know what the alkalinity really is, so stop dosing, and configure an alarm to go off elsewhere in the Apex programming.


Snoozefest_zpsu2q1ijc3.png
 

Algae invading algae: Have you had unwanted algae in your good macroalgae?

  • I regularly have unwanted algae in my macroalgae.

    Votes: 27 33.8%
  • I occasionally have unwanted algae in my macroalgae.

    Votes: 19 23.8%
  • I rarely have unwanted algae in my macroalgae.

    Votes: 7 8.8%
  • I never have unwanted algae in my macroalgae.

    Votes: 5 6.3%
  • I don’t have macroalgae.

    Votes: 20 25.0%
  • Other.

    Votes: 2 2.5%
Back
Top