2 wire system in older apartment, took landlord a month to have an electrician replace bathroom and kitchen to GFCI's.
This is when I found out we do not have a ground wire. Putting a GFCI where I plan to set up my biocube 29 scares me.


Wiring a GFCI will only protect me from getting electrocuted but not the high end equipment right?
What are my options other than hiring an electrician?
That is correct. A GFCI will only protect you.

Installing a GFCI is a fairly simple process and it will work even if you don't have a ground wire. If you have access to your breaker (or maybe fuse) box and can secure power to the outlets, it is something you can do yourself in around 15 minutes.
 

West1

Valuable Member
View Badges
Joined
Jul 26, 2016
Messages
1,945
Reaction score
633
Location
Idaho
Rating - 100%
1   0   0
That is correct. A GFCI will only protect you.

Installing a GFCI is a fairly simple process and it will work even if you don't have a ground wire. If you have access to your breaker (or maybe fuse) box and can secure power to the outlets, it is something you can do yourself in around 15 minutes.

My concern is protecting my equipment since I know I will be switching all outlets to GFCI's. I believe I have a crawl space and was thinking about grounding certain GFCI's to a copper ground rod, would this be sufficient?
 

_Alex_

Valuable Member
View Badges
Joined
Nov 22, 2009
Messages
2,109
Reaction score
87
Location
wichita, kansas
Rating - 0%
0   0   0
if any one out there has a video of someone building a t5 light from scratch, could you link it. i cant find a video. i wanted to buy all of the pieces and make it totally custom. other then a ballast, end caps and a plug what do i need? i have a some experience as a maintenance man for a hotel and i am totally confident i can wire the the ballast part because i have done it multiple times (Plus the wiring diagram is on the ballast itself). however, i have only replaced the ballast and end pins before and i am curious on what else goes into the Whole light, such as other parts or ways to cool it and i cant find any video of anyone doing it. a diagram wont help because i am not and electrical engineer and don't know how to read those.
thanks



Are you wanting something inside a canopy or a light fixture? If your wanting a "fixture" you will need to build some kind of case to hold everything in. And on a lot of lights the ballast run external now so the heat is not added on with the bulbs inside it.

If going in a canopy basically just need to mount them bulb holders and reflectors on a board inside the canopy and wire them up.
 

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,034
Location
Decatur, AL
Rating - 0%
0   0   0
My concern is protecting my equipment since I know I will be switching all outlets to GFCI's. I believe I have a crawl space and was thinking about grounding certain GFCI's to a copper ground rod, would this be sufficient?
Grounds are not installed to protect equipment. They only come in to play if the equipment has failed. Both grounds and GFCI are about people/fire protection, not equipment protection.

As for installing a ground rod, there is no way to know if a ground rod will work without doing a soil sample. You would need to ask a local electrician what is typically used in your area. It is not uncommon to need a 10ft copper ground rod if you have well draining soil.

What condition are you worried about that you are trying to protect your equipment from?
 

West1

Valuable Member
View Badges
Joined
Jul 26, 2016
Messages
1,945
Reaction score
633
Location
Idaho
Rating - 100%
1   0   0
Grounds are not installed to protect equipment. They only come in to play if the equipment has failed. Both grounds and GFCI are about people/fire protection, not equipment protection.

As for installing a ground rod, there is no way to know if a ground rod will work without doing a soil sample. You would need to ask a local electrician what is typically used in your area. It is not uncommon to need a 10ft copper ground rod if you have well draining soil.

What condition are you worried about that you are trying to protect your equipment from?

Im more worried about the unknown I guess (not an electrician). I was reading via web and I keep seeing the repeated Equipment is not safe with no ground wire. The surge will/could run to the equipment and ruin it.
First time in the saltwater hobby so I am trying to cover all areas of failure.
Doesn't help when the electrician said w/no ground wire its a very high risk.
 

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,034
Location
Decatur, AL
Rating - 0%
0   0   0
Im more worried about the unknown I guess (not an electrician). I was reading via web and I keep seeing the repeated Equipment is not safe with no ground wire. The surge will/could run to the equipment and ruin it.
First time in the saltwater hobby so I am trying to cover all areas of failure.
Doesn't help when the electrician said w/no ground wire its a very high risk.
A household outlet typically has 3 prongs. One is the hot, one is the neutral, and one is the ground. The ground and the neutral are tied together in the electrical panel. The fact that the neutral is tied to ground will protect your equipment as well as anything.
The ground plug is used for people protection. If the device you are plugging in has a metal frame or case, the ground plug is directly connected to that frame. This protects the person using the device if the hot lead shorts to the metal case inside the equipment.
If the device is completely plastic or is "double insulated" it will not even have a ground plug. Since there is no metal case to ground the ground plug serves no purpose. That is why these devices only need 2 prong plugs.

The one place a ground plug will help is if you use a power strip with built in surge protection. Those typically use the ground plug to redirect a surge from the hot lead to ground.

Personally, given that I have a choice, I would never live in a home without grounded outlets for safety reasons. I do consider it high risk. That said, not everyone has that option so it is best to understand exactly what the hazards are and to try and absolutely minimize the use of any tools/equipment that come with a ground plug.
 

Shaun Sweeney

Active Member
View Badges
Joined
Aug 5, 2016
Messages
477
Reaction score
281
Location
Lantzville, BC, Canada
Rating - 0%
0   0   0
After 25 years experiance on the field and 15 years at the office, as an electrican I think I can answer most of your questions.

Thanks to my fellow electricians for helping answering your question's.
And the team is:

Myself and
anemonekeeper



:wink:
Thanks for your offer to help. In my new install, the pumps are in the basement so I need to be able to turn them off/on from in the house, or in the basement. I picked up 3 wire switches but I'm not yet clear if I need wire that is different from the usual 15 amp house wiring to run between the switches. Many thanks.
 

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,034
Location
Decatur, AL
Rating - 0%
0   0   0
Thanks for your offer to help. In my new install, the pumps are in the basement so I need to be able to turn them off/on from in the house, or in the basement. I picked up 3 wire switches but I'm not yet clear if I need wire that is different from the usual 15 amp house wiring to run between the switches. Many thanks.
Unfortunately, the post you quoted is around 4 years old and I do not believe they are active on this site anymore.

Depending on your location and local codes, 12awg wire should be fine for this installation as long as your pump pulls less than 15 amps.
 

Shaun Sweeney

Active Member
View Badges
Joined
Aug 5, 2016
Messages
477
Reaction score
281
Location
Lantzville, BC, Canada
Rating - 0%
0   0   0
LOL .. I just keep wandering around this cool site. Thanks for the response, I'm ok with the amp draw but still wondering about how many wires are needed between the 3 wire switches. I'm guessing it's 3 plus ground.
 

Brew12

Electrical Gru
View Badges
Joined
Aug 14, 2016
Messages
22,488
Reaction score
61,034
Location
Decatur, AL
Rating - 0%
0   0   0
LOL .. I just keep wandering around this cool site. Thanks for the response, I'm ok with the amp draw but still wondering about how many wires are needed between the 3 wire switches. I'm guessing it's 3 plus ground.
That is correct, you need 3 plus the ground.

Let me add that depending on your wiring method, you may only need the 3 wire conductor between the two switches. Many different ways to make this work.
 

Paul B

10K Club member
View Badges
Joined
Nov 3, 2010
Messages
18,083
Reaction score
61,645
Location
Long Island NY
Rating - 0%
0   0   0
You need 3 including the neutral and a ground if you are using one. You may need another one depending on where the feed it. Brew is correct, there are quite a few ways to do this. Also some legal ways :eek:
3 way switches are fun and you can do a few wired things with them.
Do you know how to hook up a bell and make it work with just one wire with no cuts in it? :rolleyes:

((Master Electrician 40 years)
 

Paul B

10K Club member
View Badges
Joined
Nov 3, 2010
Messages
18,083
Reaction score
61,645
Location
Long Island NY
Rating - 0%
0   0   0
You are good!! :D
 

Turbo's Aquatics

Super Duper Member
View Badges
Joined
Jun 7, 2011
Messages
2,805
Reaction score
4,030
Location
West Des Moines, IA
Rating - 0%
0   0   0
They can't sing very well!!

But seriously
Transformer noise is caused by a phenomenon which causes a piece of magnetic sheet steel to extend itself when magnetized. When the magnetization is taken away, it goes back to its original condition. This phenomenon is scientifically referred to as magnetostriction. A transformer is magnetically excited by an alternating voltage and current so that it becomes extended and contracted twice during a full cycle of magnetization.

The magnetization of any given point on the sheet varies, so the extension and contraction is not uniform. A transformer core is made from many sheets of special steel to reduce losses and moderate the ensuing heating effect. The extensions and contractions are taking place erratically all over a sheet and each sheet is behaving erratically with respect to its neighbor, so you can see what a moving, writhing construction it is when excited. These extensions are miniscule proportionally and therefore not normally visible to the naked eye. However, they are sufficient to cause a vibration, and consequently noise. Applying voltage to a transformer produces a magnetic flux, or magnetic lines of force in the core. The degree of flux determines the amount of magnetostriction and hence, the noise level.
 

West1

Valuable Member
View Badges
Joined
Jul 26, 2016
Messages
1,945
Reaction score
633
Location
Idaho
Rating - 100%
1   0   0
A household outlet typically has 3 prongs. One is the hot, one is the neutral, and one is the ground. The ground and the neutral are tied together in the electrical panel. The fact that the neutral is tied to ground will protect your equipment as well as anything.
The ground plug is used for people protection. If the device you are plugging in has a metal frame or case, the ground plug is directly connected to that frame. This protects the person using the device if the hot lead shorts to the metal case inside the equipment.
If the device is completely plastic or is "double insulated" it will not even have a ground plug. Since there is no metal case to ground the ground plug serves no purpose. That is why these devices only need 2 prong plugs.

The one place a ground plug will help is if you use a power strip with built in surge protection. Those typically use the ground plug to redirect a surge from the hot lead to ground.

Personally, given that I have a choice, I would never live in a home without grounded outlets for safety reasons. I do consider it high risk. That said, not everyone has that option so it is best to understand exactly what the hazards are and to try and absolutely minimize the use of any tools/equipment that come with a ground plug.

Thx for the details.
We moved here temporarily due to High School, renting our house out that has 100% new electrical.

I did not even think to review the electrical when we moved into this 2yr lease.
 

Awesome Dennis

Well-Known Member
View Badges
Joined
Sep 16, 2016
Messages
651
Reaction score
539
Rating - 0%
0   0   0
Are the boxes in the wall holding the outlets metal or plastic?
 

High pressure shells: Do you look for signs of stress in the invertebrates in your reef tank?

  • I regularly look for signs of invertebrate stress in my reef tank.

    Votes: 11 37.9%
  • I occasionally look for signs of invertebrate stress in my reef tank.

    Votes: 9 31.0%
  • I rarely look for signs of invertebrate stress in my reef tank.

    Votes: 4 13.8%
  • I never look for signs of invertebrate stress in my reef tank.

    Votes: 5 17.2%
  • Other.

    Votes: 0 0.0%
Back
Top