Hi,
I have a GHL Profilux 4 and want to confirm that I understand temperature control correctly. I'm using a Colbalt Neo-Therm as the main control, then the P4 to turn off the heater if it gets too hot. I'm not using the P4 as the main control since I do not want the main power constantly cycling the Cobalt on and off. The Cobalt would then be starting up and shutting down each time, and that is probably not the best thing for it's electronics.
Here's my settings in the P4:
Nominal = 78.8F
Cooling Difference = 0.0F
Hysteresis = 0.4F
0-10V Max = 1.6F
The Cobalt is set at 78F.
I programmed an outlet on the Powerbar as a Heater.
Is my understanding of the following correct?
I have a GHL Profilux 4 and want to confirm that I understand temperature control correctly. I'm using a Colbalt Neo-Therm as the main control, then the P4 to turn off the heater if it gets too hot. I'm not using the P4 as the main control since I do not want the main power constantly cycling the Cobalt on and off. The Cobalt would then be starting up and shutting down each time, and that is probably not the best thing for it's electronics.
Here's my settings in the P4:
Nominal = 78.8F
Cooling Difference = 0.0F
Hysteresis = 0.4F
0-10V Max = 1.6F
The Cobalt is set at 78F.
I programmed an outlet on the Powerbar as a Heater.
Is my understanding of the following correct?
- After entering those values I see slightly different numbers for hysteresis and 0-10V max. This is because the increments in the program are in C, and the conversion to F causes this? For example, hysteresis is 0.396F, not the 0.4F that I entered.
- The heater will turn on at 78.6F and off at 79.0F?
- The cooling fans (PropellerBreeze) will turn on at 79.1F? (T=nom+5/6*hys +cooling diff)
- The fans will reach max speed at 80F? (T=nom+5/6*hys+0-10V max)
Nominal = 78.08F (entered 78F, it converted to 78.08F)
Cooling Difference = 0.0F
Hysteresis = 0.270F (min setting)
0-10V Max = 3.6F (value does not affect alarms)
Alarm = Active
Deactivate Control = No
Max deviation +/- = 0.9F (min setting)
Cooling Difference = 0.0F
Hysteresis = 0.270F (min setting)
0-10V Max = 3.6F (value does not affect alarms)
Alarm = Active
Deactivate Control = No
Max deviation +/- = 0.9F (min setting)
- Low Alarm will be 77.05F? (AL = nom-1/2*hys-dev)
- High Alarm will be 79.21F? (AH = nom+5/6*hys+dev+cooling diff)