You would be just fine with a GFCI breaker. Some people prefer them because they are considered less likely to fail.
good to know was curious why everyone talks about changing the oulet, when can do the breaker and be done easy everywhere
If it was me, I would change the breaker.....good to know was curious why everyone talks about changing the oulet, when can do the breaker and be done easy everywhere
One very good reason I have seen is when people cannot access a receptacle behind the tank. It is easier to change the breaker to GFCI than to find an upstream receptacle and change it out.Outlet is cheaper.
Outlet is lower risk of shock. Working off of single de-energized cct vs working in panel.
Outlet can protect all additional outlets downstream from it, if you need it too.
There really is no reason to use a breaker.
One very good reason I have seen is when people cannot access a receptacle behind the tank. It is easier to change the breaker to GFCI than to find an upstream receptacle and change it out.
or thisScenario 1. Hot line to water via submerged equipment. This is when a submerged piece of equipment like a powerhead, heater or UV lamp fails and the hot line of the power supply gets in contact with the water:
c) GROUND PROBE INSTALLED BUT NO GFCI (Our case of discussion in this thread): As soon as the device fails and a short circuit is established then current is established to the ground probe, current may or may not be high enough to trip the breaker. Fish and critters will die and corals will RTN. If the breaker does not trip (Which is most of the cases) the short circuit may not be noticeable and you will be at a loss of why your critters are dying, even if you touch the water you may not notice unless the ground probe is not making a good ground. (See also Scenario 3c below) This is also a dangerous situation for potential fire. The current could be high but not high enough to trip the breaker, wires heat up, insulation melts and they catch fire.
or thisScenario 2: Short circuit between hot line and neutral on submerged equipment:
c) Ground probe installed but no GFCI: Same situation as in 2a above but if a secondary short is created current will be established killing the tank inhabitants but just probably faster than the toxic chemicals or copper compounds. Here you are dependent on the breaker.
or thisScenario 3: Short circuit from hot to a metal part of a non-submerged device and there is no current to trip the device as the metal body is not grounded: This is typical of a lighting fixture to whom one of the light bulb wires touches the reflector or the metallic hood or when some of the wiring of external pumps short to the pumps body and the body of the pump is not grounded.
c) Ground probe and no GFCI: This is one of the the main reasons why probes shall not be installed unless a GFCI is also installed. The water will be perfectly grounded. If you are working in the water and touch the device you will get badly shocked or electrocuted even is you yourself are electrically insulated by the use of rubber soles or such.
Scenario 5: Short from Neutral to water: As usually the neutral wire is grounded either at the outside were the wires enter the house or at the main nothing happens unless this neutral grounding is not perfect some small voltage may develop creating the following situation:
c) Ground probe but no GFCI: The small voltage may create a permanent small current, this may be enough to start killing the most sensitive critters, (Pods and Snails) and create coral RTN over long term.
I really want to take more time to dig into this and address what you have written, including the older post you have referenced. Unfortunately, I don't have time to get into that right now. The one thing I do want to quickly say is that where the ground probe plugs into the system has no impact on any fault conditions. All of the house grounds, including properly designed power strips that are plugged in, should always be connected and are not disconnected by a GFCI opening. A GFCI also does not care where the ground current flows since it doesn't measure ground current. If the faulted device is inside the zone covered by the GFCI it will trip even if the ground probe is plugged into a separate circuit on the house. If the faulted device is on an outlet before the GFCI, no GFCI trip will occur even if the ground probe is plugged into a GFCI protected outlet.Now, what happens when there is a ground fault on another device in the system? The way I see it, this would not trip the GFCI because the fault needs to happen on what is connected to the device itself. So in essence, placing a ground probe on a GFCI that is at the tail end of the circuit run can actually act like the scenario where you have a ground probe and no GFCI, which can lead to this:
Personally, I feel that the fear of high current from using a ground probe without a GFCI is overblown. If you have a heater or motor casing crack, the water will short between the the hot to the neutral. In this case, the neutral is the exact same thing as a ground probe.Right...that was my point, I guess.
Obviously, if the faulty device trips the GFCI, it will no longer have power, thus no current (from that device's fault) would go through the ground probe.
This basically raises the issue of GFCI & ground probe when all devices are not on the GFCI. This is a situation where one could think they are protected, when in fact they are not, and in a way that specifically could start a fire under certain circumstances.
Kinda leads you to the "all or nothing" type of philosophy. Either you have everything on GFCI and then have a ground probe, or you only have certain devices on GFCI and no ground probe. But you can't have it both ways.
Seems like the missing element here is a current sensor on the ground...something that wouldn't shut everything off, but would sound an alarm to let the aquarist know that something is not right = don't reach into the tank!
If you are so concerned about a faulty pump on a gfci tripping then get an external pump.
If I absolutely could not put in a GFCI but decided to add a ground probe I would not connect it (ground it), instead I would use it as a fault indicator and connect one end of the ground to a light bulb or led and the other to ground. My selected voltage would probably be 48v to signal fault situation.
Curious: why does this make a difference? Can't an external pump have a situation that would trip a GFCI?If you are so concerned about a faulty pump on a gfci tripping then get an external pump.
It can, but since the pump isn't in the tank it will not leak voltage/current into the tank.Curious: why does this make a difference? Can't an external pump have a situation that would trip a GFCI?
An external pump will not be subjected to constant contact with salt water and will more than likely never fail. (The motor windings that is, not the bearings, pump seal, etc.)Curious: why does this make a difference? Can't an external pump have a situation that would trip a GFCI?